NICEIC Area E


Join the forum, it's quick and easy

NICEIC Area E
NICEIC Area E
Would you like to react to this message? Create an account in a few clicks or log in to continue.
Search
 
 

Display results as :
 


Rechercher Advanced Search

Keywords

Latest topics
» I.T. system - medical locations
Solar PV Inverter Circuits and the possible need for RCD Protection EmptySun Dec 02, 2012 9:00 am by Andy B

» regulation 537.1.4
Solar PV Inverter Circuits and the possible need for RCD Protection EmptyFri Sep 07, 2012 3:59 am by iant

» Flashing LED Lamps on Two Way Switched Circuits
Solar PV Inverter Circuits and the possible need for RCD Protection EmptyThu Aug 23, 2012 8:26 am by terry gray

» The Long Lead (R2) Continuity Test for Periodic Inspections
Solar PV Inverter Circuits and the possible need for RCD Protection EmptyWed Aug 22, 2012 5:31 pm by terry gray

» The Importance of Providing Layout Diagrams and Labelling
Solar PV Inverter Circuits and the possible need for RCD Protection EmptyTue Aug 21, 2012 5:22 pm by terry gray

» Shocking experience whats the explanation?
Solar PV Inverter Circuits and the possible need for RCD Protection EmptyTue Aug 21, 2012 8:51 am by Dunc

» Use of a Voltage Detector as a Means of Quickly Finding Unearthed Metalwork
Solar PV Inverter Circuits and the possible need for RCD Protection EmptyTue Aug 21, 2012 6:25 am by terry gray

» Certificates
Solar PV Inverter Circuits and the possible need for RCD Protection EmptyMon Aug 20, 2012 5:33 pm by terry gray

» Use of an A.C. Milli-Amp Clampmeter for Fault Finding Purposes
Solar PV Inverter Circuits and the possible need for RCD Protection EmptyWed Aug 15, 2012 8:39 am by terry gray

April 2024
MonTueWedThuFriSatSun
1234567
891011121314
15161718192021
22232425262728
2930     

Calendar Calendar

Affiliates
free forum

Affiliates
free forum


Solar PV Inverter Circuits and the possible need for RCD Protection

Go down

Solar PV Inverter Circuits and the possible need for RCD Protection Empty Solar PV Inverter Circuits and the possible need for RCD Protection

Post by terry gray Tue Apr 03, 2012 8:20 am

RCD’s and RCBO’s as we know are excellent devices for protection against shock (known as additional protection) and line earth faults (known as fault protection). RCD’s are also used to provide an early warning of insulation break down to prevent a fire. The question is are they necessary to cover Solar PV circuits? Having said that, generally there are only a couple of instances where they will be required in a domestic property by BS 7671:2008, for example, if the wiring method is a Twin & Earth cable buried in the fabric of the wall less than 50mm deep (additional protection) or if the building is fed from a TT system (fault protection). Other than that there is no specific requirement to protect Solar pv circuits with RCD/RCBO protection. In fact, I advise installers to avoid RCD protection altogether if possible, especially using a 30mA device, as many inverters are now electronic and leak to earth by nature, which will make the circuit prone to nuisance tripping.

To negate the use of an RCD/RCBO on Solar PV circuits in terms of burying a cable in a wall, I would suggest the use of a Flexi Shield cable to BS 8436 or a cable which has an earthed metallic sheath under Clause (i) Reg 522.6.101 on pg 124, or one of the other options clause (ii to iv). To avoid the requirement for RCD protection altogether Reg 522.6.102 pg 125, simply running the cable on the surface in robust wiring system or a containment system such as plastic conduit or trunking, would be a solution.

If it is not possible to avoid the use of RCD protection on say a TT system (fault protection), then as Reg 712.411.3.2.1.2 on pg 242 suggests a Type B (ideally a 100 mA device - although it doesn’t say that) would be necessary, as a leakage current to earth due to a fault downstream from the device may not be sinusoidal in nature. If the inverter does not have simple separation ie a transformer (possibly galvanic isolation) or some other fail safe technology (Ref the manufacturer), then an earth leakage current may be pulsed or pure DC in nature, which a general Type AC RCD will not pick-up and thus fail to operate. This is why the aforementioned Reg requires a Type B device is installed, which will sense AC, half wave DC and pure DC leakage currents. The different types of RCD are very often denoted by a symbol in a box on the front of the device. Incidentally, the Type B device is hard to obtain, is relatively expensive, and the installer will require a test instrument that can perform a Type B RCD test. In addition, RCD’s and RCBO’s will have to be double pole devices to avoid the situation shown on page 14 of the ESC Best Practice guide.

In terms of good practice, if an installer cannot avoid using an RCD/RCBO protection, or even without - the preferred option is to install a separate DB dedicated only to the solar PV circuit. By doing this the installer will keep any problems with either the general consumer unit or PV supply DB completely independent of each other. Of course this does not rule out any other options, but to my mind this is the ideal solution and would also provide a safer isolation procedure for maintenance/servicing in terms of two supplies coming into one DB.

terry gray