NICEIC Area E


Join the forum, it's quick and easy

NICEIC Area E
NICEIC Area E
Would you like to react to this message? Create an account in a few clicks or log in to continue.
Search
 
 

Display results as :
 


Rechercher Advanced Search

Keywords

Latest topics
» I.T. system - medical locations
Electrical Installation Condition Report - Cover Sheet EmptySun Dec 02, 2012 9:00 am by Andy B

» regulation 537.1.4
Electrical Installation Condition Report - Cover Sheet EmptyFri Sep 07, 2012 3:59 am by iant

» Flashing LED Lamps on Two Way Switched Circuits
Electrical Installation Condition Report - Cover Sheet EmptyThu Aug 23, 2012 8:26 am by terry gray

» The Long Lead (R2) Continuity Test for Periodic Inspections
Electrical Installation Condition Report - Cover Sheet EmptyWed Aug 22, 2012 5:31 pm by terry gray

» The Importance of Providing Layout Diagrams and Labelling
Electrical Installation Condition Report - Cover Sheet EmptyTue Aug 21, 2012 5:22 pm by terry gray

» Shocking experience whats the explanation?
Electrical Installation Condition Report - Cover Sheet EmptyTue Aug 21, 2012 8:51 am by Dunc

» Use of a Voltage Detector as a Means of Quickly Finding Unearthed Metalwork
Electrical Installation Condition Report - Cover Sheet EmptyTue Aug 21, 2012 6:25 am by terry gray

» Certificates
Electrical Installation Condition Report - Cover Sheet EmptyMon Aug 20, 2012 5:33 pm by terry gray

» Use of an A.C. Milli-Amp Clampmeter for Fault Finding Purposes
Electrical Installation Condition Report - Cover Sheet EmptyWed Aug 15, 2012 8:39 am by terry gray

March 2024
MonTueWedThuFriSatSun
    123
45678910
11121314151617
18192021222324
25262728293031

Calendar Calendar

Affiliates
free forum

Affiliates
free forum


Electrical Installation Condition Report - Cover Sheet

2 posters

Go down

Electrical Installation Condition Report - Cover Sheet Empty Electrical Installation Condition Report - Cover Sheet

Post by terry gray Fri Apr 20, 2012 6:37 am

In my travels around the region undertaking A/C assessments, a lot of contractors ask my opinion about the use of Electrical Installation Condition Reports - in particular what should they do when a client asks for a so called 'clean report' for insurance or other purposes? Firstly, I tell them that they should not be dictated to by the client about what they should, or should not record on the document, as its purpose is to faithfully detail every defect found in an existing installation. They then go on to ask if they undertake remedial works at the same time as the periodic inspection can they issue a clean report?

Having given this matter some thought, I felt that there was a compromise to be made in the form of a cover sheet I've called a Declaration of Conformity' - please see draft sample below. This idea is not a new one and has been discussed before at NICEIC H.O., but for some reason kicked into the long grass!

The idea of using this document is to confirm that the electrical installation is in a SATISFACTORY condition following remedial work for which appropriate Minor Works or Electrical Installation Certificates have been issued. These documents can then be bundled with the report together with the Declaration of Conformity on top stating the electrical installation is now deemed to be in a safe condition. This document has been used by some of my contractors who think it is a very useful. A draft version of the document below is also currently under consideration by the NICEIC technical panel a copy of which is available on request terry.gray@niceic.com.

Declaration of Conformity

The following work has been carried out in reference to the Electrical Installation Condition Report detailed below.
Any work carried out on this report should also be accompanied by the relevant certification, i.e. Minor Works, Installation Certificate, Fire Detection certificates etc.
Address


Post Code

Section A: Details of Original certification this report relates to.
Report type Report Number Report Date


Section B: The following work was carried out as per observation sheet of above report.
Work description (Work carried out) Date complete Previous Item number Related certification No.
i.e. Replaced broken socket (front bedroom) 01/01/2011 2 IMN2 / 123456











Section C: Details of observations still outstanding.
The work below is still outstanding as per previous report.
Work Description (Work still outstanding ) Previous Item number Code






Section D: Assessment
This property is now seen to be in SATISFACTORY condition.

Section E: Declaration

Signature……………………………. Name (Capitals)…………………………...

Position……………………………… Date………………………………………..



terry gray

Posts : 16
Join date : 2012-02-29

Back to top Go down

Electrical Installation Condition Report - Cover Sheet Empty Re: Electrical Installation Condition Report - Cover Sheet

Post by yvonnew Sun Jun 03, 2012 12:32 am

Hi Terry yes I get the same query regarding remedials etc and 'clean' PIRs etc can you email the document to me so I can take a look?
What I have been saying to the contractors I visit if this is raised is to recorde the observation and code it accordingly and then right RECTIFIED after the observation as this is then a recored of the defect and the fact it has been repaired correctly then the PIR could state satisifactory

yvonnew

Posts : 7
Join date : 2012-02-29