Can Voltage Optimisers be installed along side Solar PV systems?
NICEIC Area E :: MCS
Page 1 of 1
Can Voltage Optimisers be installed along side Solar PV systems?
My initial reaction to this question was probably no! However, after a bit of Googling I came across a company that seem to be one of the market leaders called Vphase who say that their voltage optimizer can be used in conjunction with a Solar PV system provided the pv system is connected upstream to the optimizer. More details can be seen on the company web site at http://www.vphase.co.uk/how-it-works/solar-pv-and-vphase or contact 0845 033 8222.
Apparently, these devices have a toroidial transformer wound in anti-phase that subtracts a desired value from the supply voltage, generally giving an output of 220 volts. The units can handle up to 2 kW in a domestic installation and will go into bypass mode should the load drawn be in excess of 2kW.
The question has been asked regarding whether or not an earth loop test can be conducted through the V-Phase unit? The technical department at V phase have confirmed that it is possible to conduct the test, but the unit will add about 0.2 ohms to the reading and the Max Zs reference values will need to be adjusted for 220 volts.
Much larger 3 phase voltage optomiser units are now being installed in commercial and industrial buildings (typically 150 -250 kVA) which are thyristor controlled and they act somewhat like a large UPS system that is connected in series with the load to be controlled. Again, the supply voltage is dropped to a Uo of 220 Volts and should the input supply voltage fall below 220 V, these units will increase their output voltage to compensate for the short-fall.
Apparently, these devices have a toroidial transformer wound in anti-phase that subtracts a desired value from the supply voltage, generally giving an output of 220 volts. The units can handle up to 2 kW in a domestic installation and will go into bypass mode should the load drawn be in excess of 2kW.
The question has been asked regarding whether or not an earth loop test can be conducted through the V-Phase unit? The technical department at V phase have confirmed that it is possible to conduct the test, but the unit will add about 0.2 ohms to the reading and the Max Zs reference values will need to be adjusted for 220 volts.
Much larger 3 phase voltage optomiser units are now being installed in commercial and industrial buildings (typically 150 -250 kVA) which are thyristor controlled and they act somewhat like a large UPS system that is connected in series with the load to be controlled. Again, the supply voltage is dropped to a Uo of 220 Volts and should the input supply voltage fall below 220 V, these units will increase their output voltage to compensate for the short-fall.
terry gray- Posts : 16
Join date : 2012-02-29
Similar topics
» Use of a Voltage Detector as a Means of Quickly Finding Unearthed Metalwork
» DC Isolators for Solar PV
» Solar PV Inverter Circuits and the possible need for RCD Protection
» earthing Array and TL inverters
» Location of Solar PV Inverters and preventing the risk of fire.
» DC Isolators for Solar PV
» Solar PV Inverter Circuits and the possible need for RCD Protection
» earthing Array and TL inverters
» Location of Solar PV Inverters and preventing the risk of fire.
NICEIC Area E :: MCS
Page 1 of 1
Permissions in this forum:
You cannot reply to topics in this forum
|
|
Sun Dec 02, 2012 9:00 am by Andy B
» regulation 537.1.4
Fri Sep 07, 2012 3:59 am by iant
» Flashing LED Lamps on Two Way Switched Circuits
Thu Aug 23, 2012 8:26 am by terry gray
» The Long Lead (R2) Continuity Test for Periodic Inspections
Wed Aug 22, 2012 5:31 pm by terry gray
» The Importance of Providing Layout Diagrams and Labelling
Tue Aug 21, 2012 5:22 pm by terry gray
» Shocking experience whats the explanation?
Tue Aug 21, 2012 8:51 am by Dunc
» Use of a Voltage Detector as a Means of Quickly Finding Unearthed Metalwork
Tue Aug 21, 2012 6:25 am by terry gray
» Certificates
Mon Aug 20, 2012 5:33 pm by terry gray
» Use of an A.C. Milli-Amp Clampmeter for Fault Finding Purposes
Wed Aug 15, 2012 8:39 am by terry gray