NICEIC Area E


Join the forum, it's quick and easy

NICEIC Area E
NICEIC Area E
Would you like to react to this message? Create an account in a few clicks or log in to continue.
Search
 
 

Display results as :
 


Rechercher Advanced Search

Keywords

Latest topics
» I.T. system - medical locations
Flashing LED Lamps on Two Way Switched Circuits EmptySun Dec 02, 2012 9:00 am by Andy B

» regulation 537.1.4
Flashing LED Lamps on Two Way Switched Circuits EmptyFri Sep 07, 2012 3:59 am by iant

» Flashing LED Lamps on Two Way Switched Circuits
Flashing LED Lamps on Two Way Switched Circuits EmptyThu Aug 23, 2012 8:26 am by terry gray

» The Long Lead (R2) Continuity Test for Periodic Inspections
Flashing LED Lamps on Two Way Switched Circuits EmptyWed Aug 22, 2012 5:31 pm by terry gray

» The Importance of Providing Layout Diagrams and Labelling
Flashing LED Lamps on Two Way Switched Circuits EmptyTue Aug 21, 2012 5:22 pm by terry gray

» Shocking experience whats the explanation?
Flashing LED Lamps on Two Way Switched Circuits EmptyTue Aug 21, 2012 8:51 am by Dunc

» Use of a Voltage Detector as a Means of Quickly Finding Unearthed Metalwork
Flashing LED Lamps on Two Way Switched Circuits EmptyTue Aug 21, 2012 6:25 am by terry gray

» Certificates
Flashing LED Lamps on Two Way Switched Circuits EmptyMon Aug 20, 2012 5:33 pm by terry gray

» Use of an A.C. Milli-Amp Clampmeter for Fault Finding Purposes
Flashing LED Lamps on Two Way Switched Circuits EmptyWed Aug 15, 2012 8:39 am by terry gray

April 2024
MonTueWedThuFriSatSun
1234567
891011121314
15161718192021
22232425262728
2930     

Calendar Calendar

Affiliates
free forum

Affiliates
free forum


Flashing LED Lamps on Two Way Switched Circuits

Go down

Flashing LED Lamps on Two Way Switched Circuits Empty Flashing LED Lamps on Two Way Switched Circuits

Post by terry gray Thu Aug 23, 2012 8:26 am

This is an occasional observation with both LED and CFL lighting on two-way switched circuits and is a frequent topic on IEE and electrician’s discussion forums. It is not a fault with the lamps.

This issue is normally a result of capacitive coupling between the live and switched live wires running between the two-way switches. The capacitive coupling causes a build-up of charge within the lamp which is then released when it reaches a certain level causing the lamp to flash. The cycle then repeats. This is a safe if not ideal situation created by historically common wiring methods which enable capacitive coupling. The effect has not been apparent with filament lighting as the charge can dissipate without any noticeable illumination of the lamp but is highlighted by the sensitivity of modern low energy lamps.

The phenomenon does not affect all two-way switched circuits and is often reduced or non-existent when there is a connected earth conductor running between the strapper wires, or the wires are widely separated.

If there is more than one lamp on the circuit the diagnosis can be confirmed by replacing one of the lamps with a filament lamp as the additional resistive load will prevent the LED lamp from building-up a charge. In addition, with the switches off, there will probably be a detectable voltage on the switched live wire to the lamp in one of the off configurations.

There are two approaches to solving the problem:

1) A suppressor (or snubber) can be added to the circuit between the switched live and neutral in parallel with the lamps and as close to the last lamp as possible, possibly within one of the fitting itself or the ceiling rose. This a cheap solution and a suppressor such as this can be used:http://www.maplin.co.uk/contact-suppressor-498

2]A resistive load which mimics the action of the halogen lamp as mentioned above can be added in parallel with the lamps but this is a more expensive solution.


Last edited by terry gray on Thu Aug 23, 2012 8:33 am; edited 1 time in total (Reason for editing : Update)